An elevator hoistway has sprinklers. Where must heat detectors for shunt trip be located?

Exactly one answer is correct.

Show solution

Correct answer to question 4030

  • C: Within 2 ft of each sprinkler

Explanation

Heat detectors used for elevator power shutdown must be within 24 in. of each sprinkler in the hoistway or machine room. They must have a lower temperature rating and higher sensitivity than the sprinklers so power is removed first.