Question 4030 of 243 · NICET Fire Alarm Systems Level IV
An elevator hoistway has sprinklers. Where must heat detectors for shunt trip be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4030
- C: Within 2 ft of each sprinkler
Explanation
Heat detectors used for elevator power shutdown must be within 24 in. of each sprinkler in the hoistway or machine room. They must have a lower temperature rating and higher sensitivity than the sprinklers so power is removed first.