Before testing a releasing system in an occupied data center, what should the technician do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4026
- C: Disconnect or isolate the actuators and notify the owner and monitoring
Explanation
Testing a releasing system without isolating actuators risks an accidental discharge. The technician uses disconnects or substitute loads, coordinates with the owner and the supervising station, and restores the system afterward.