Question 4026 of 243 · NICET Fire Alarm Systems Level IV

Before testing a releasing system in an occupied data center, what should the technician do?

Exactly one answer is correct.

Show solution

Correct answer to question 4026

  • C: Disconnect or isolate the actuators and notify the owner and monitoring

Explanation

Testing a releasing system without isolating actuators risks an accidental discharge. The technician uses disconnects or substitute loads, coordinates with the owner and the supervising station, and restores the system afterward.

Next to question ›