A designer wants to use a waterflow switch to initiate shunt trip. What restriction applies?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4031
- C: It must have no time delay feature
Explanation
Where a waterflow switch initiates elevator power shutdown, it must not have time delay capability. Power must be removed before water reaches the elevator equipment.