Question 4032 of 243 · NICET Fire Alarm Systems Level IV
What must be monitored for integrity in an elevator shunt trip circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4032
- D: The control circuit voltage of the shunt trip breaker
Explanation
The code requires the power to the shunt trip control circuit to be monitored for integrity. A loss of that power would prevent the breaker from tripping when needed.