For a non-voice fire alarm system, what secondary power capacity does NFPA 72 require?

Exactly one answer is correct.

Show solution

Correct answer to question 3001

  • A: 24 hours of standby followed by 5 minutes of alarm

Explanation

NFPA 72 requires the secondary supply to run the system under quiescent load for 24 hours and then operate all alarm notification appliances for 5 minutes. The 15 minute figure applies to emergency voice/alarm systems.