Question 3010 of 183 · Ohio Fire Alarm Certification Exam
An open occurs in the middle of a Class B initiating device circuit. What is the result?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3010
- A: A trouble signal, and devices beyond the open cannot report alarms
Explanation
Class B has no redundant path. The end of line supervision detects the open and gives a trouble signal, but devices past the break are cut off until the fault is repaired.
More questions: Circuits, Power Supplies and Control Units
- 3011What does pathway survivability Level 2 generally require?
- 3012A ground fault develops on a monitored fire alarm pathway. What must the system do?
- 3013What is the purpose of an end of line resistor on a conventional initiating device circuit?
- 3014Which article of NFPA 70 (National Electrical Code) covers the wiring of fire alarm systems?
- 3015A trouble signal is silenced at the control unit but the fault is not fixed. What must happen?