Which article of NFPA 70 (National Electrical Code) covers the wiring of fire alarm systems?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3014
- C: Article 760
Explanation
NFPA 72 requires installation per NFPA 70, and Article 760 covers fire alarm systems including power limited and non power limited fire alarm circuits. Article 725 covers other Class 1, 2 and 3 circuits.
More questions: Circuits, Power Supplies and Control Units
- 3015A trouble signal is silenced at the control unit but the fault is not fixed. What must happen?
- 3016From what source must the primary power for a fire alarm system come?
- 3017A panel draws 0.25 A in standby and 1.2 A in alarm. With 24 hours standby and 5 minutes alarm, what capacity is needed before margin?
- 3018A voice system draws 1 A in standby and 4 A in alarm. With 24 hours standby and 15 minutes alarm, what capacity is needed before margin?
- 3019A notification circuit runs 500 feet out to the last appliance. The wire has 2 ohms per 1,000 feet. What is the total loop resistance?
- 3020A 24 V notification circuit has a 3 V drop. What percentage of the supply voltage is lost?