Question 3015 of 183 · Ohio Fire Alarm Certification Exam

A trouble signal is silenced at the control unit but the fault is not fixed. What must happen?

Exactly one answer is correct.

Show solution

Correct answer to question 3015

  • D: The trouble signal resounds at intervals of no more than 24 hours

Explanation

NFPA 72 requires a silenced trouble signal to resound at intervals not exceeding 24 hours until the condition is restored, so a fault is not forgotten.