Question 3015 of 183 · Ohio Fire Alarm Certification Exam
A trouble signal is silenced at the control unit but the fault is not fixed. What must happen?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3015
- D: The trouble signal resounds at intervals of no more than 24 hours
Explanation
NFPA 72 requires a silenced trouble signal to resound at intervals not exceeding 24 hours until the condition is restored, so a fault is not forgotten.
More questions: Circuits, Power Supplies and Control Units
- 3016From what source must the primary power for a fire alarm system come?
- 3017A panel draws 0.25 A in standby and 1.2 A in alarm. With 24 hours standby and 5 minutes alarm, what capacity is needed before margin?
- 3018A voice system draws 1 A in standby and 4 A in alarm. With 24 hours standby and 15 minutes alarm, what capacity is needed before margin?
- 3019A notification circuit runs 500 feet out to the last appliance. The wire has 2 ohms per 1,000 feet. What is the total loop resistance?
- 3020A 24 V notification circuit has a 3 V drop. What percentage of the supply voltage is lost?
- 3021Why do notification circuit voltage drop calculations often start from 20.4 V instead of 24 V?