Under NEC Article 760, how far must power limited fire alarm cables generally be kept from electric light and power conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3027
- C: At least 2 inches
Explanation
NEC 760.136 requires power limited fire alarm conductors to be separated at least 2 in (50 mm) from electric light, power, Class 1 and non power limited fire alarm conductors, unless a listed barrier or raceway separates them.
More questions: Circuits, Power Supplies and Control Units
- 3028Which power limited fire alarm cable type is listed for use in plenums?
- 3029The fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
- 3030What is the main feature of a Class C pathway?
- 3001For a non-voice fire alarm system, what secondary power capacity does NFPA 72 require?
- 3002What alarm duration must the secondary power of an in-building emergency voice/alarm communication system support after 24 hours of standby?
- 3003A panel draws 0.5 A in standby and 3 A in alarm. Using 24 hours standby and 5 minutes alarm, what is the required capacity before any safety margin?