Question 3024 of 183 · Ohio Fire Alarm Certification Exam
Which wiring method is not allowed on a supervised initiating device circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3024
- D: Looping the wire under one terminal without breaking it
Explanation
NFPA 72 requires the wire to be broken at each terminal connection so that removing a device or a loose wire produces a trouble signal. A wire looped unbroken under a screw would hide a missing device.
More questions: Circuits, Power Supplies and Control Units
- 3025How must the outgoing and return conductors of a Class A pathway generally be routed?
- 3026Which pathway class was added to NFPA 72 for Ethernet network infrastructure?
- 3027Under NEC Article 760, how far must power limited fire alarm cables generally be kept from electric light and power conductors?
- 3028Which power limited fire alarm cable type is listed for use in plenums?
- 3029The fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
- 3030What is the main feature of a Class C pathway?