The fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3029
- B: Automatic smoke detection to protect the control unit
Explanation
NFPA 72 requires automatic smoke detection at the location of the control unit, notification appliance power extenders and supervising station transmitting equipment where those areas are not continuously occupied. A heat detector may be used where smoke detection is not suitable.
More questions: Circuits, Power Supplies and Control Units
- 3030What is the main feature of a Class C pathway?
- 3001For a non-voice fire alarm system, what secondary power capacity does NFPA 72 require?
- 3002What alarm duration must the secondary power of an in-building emergency voice/alarm communication system support after 24 hours of standby?
- 3003A panel draws 0.5 A in standby and 3 A in alarm. Using 24 hours standby and 5 minutes alarm, what is the required capacity before any safety margin?
- 3004A battery calculation gives 10 ampere hours. NFPA 72 (2022) requires an aging correction factor of 1.25. What battery capacity is needed at minimum?
- 3005A notification circuit draws 2 A and the total resistance of both conductors is 1.5 ohms. What is the voltage drop on the circuit?