Non restorable fixed temperature spot type heat detectors have been in service for 15 years. What does NFPA 72 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6006
- B: Replace them or send 2 per 100 to a lab for testing
Explanation
After 15 years NFPA 72 requires replacement or laboratory testing of 2 detectors per 100 (minimum 2). If one fails, more must be tested; testing repeats every 5 years.