A heat detector with a listed spacing of 50 ft is installed on a smooth ceiling 15 ft high. Using the ceiling height reduction factor of 0.77 for ceilings over 14 ft up to 16 ft, what is the adjusted spacing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3005
- D: 38.5 ft
Explanation
Above 10 ft, the listed spacing of heat detectors is reduced by the table multiplier. 50 ft x 0.77 = 38.5 ft. No reduction applies at or below 10 ft.