Oklahoma Fire Alarm Technician Exam, System Layout and NFPA 72 Requirements: all 33 questions
All questions from the System Layout and NFPA 72 Requirements section for Oklahoma Fire Alarm Technician Exam, each with the correct answer.
- 3001What is the nominal spacing used for spot-type smoke detectors on a smooth, flat ceiling when no other spacing is required by the manufacturer?
- 3002A spot-type smoke detector is to be mounted on a sidewall instead of the ceiling. Where must the top of the detector be?
- 3003A spot-type heat detector is mounted on a sidewall. What mounting zone is permitted?
- 3004A heat detector has a listed spacing of 50 ft. What is the maximum distance from a wall to the nearest detector on a smooth ceiling?
- 3005A heat detector with a listed spacing of 50 ft is installed on a smooth ceiling 15 ft high. Using the ceiling height reduction factor of 0.77 for ceilings over 14 ft up to 16 ft, what is the adjusted spacing?
- 3006On a solid joist ceiling, how is heat detector spacing measured at right angles to the joists adjusted?
- 3007Under a peaked ceiling, where must a row of spot-type smoke detectors be placed?
- 3008A heat detector should have a temperature rating at least how far above the maximum expected ambient ceiling temperature?
- 3009A heat detector frame is colored white. Which temperature classification does this color code indicate?
- 3010NFPA 72 guidance on locating a smoke detector near an air supply diffuser calls for what minimum separation?
- 3011What is the primary purpose of a duct smoke detector in an HVAC system?
- 3012What is the required mounting height for the operable part of a manual fire alarm box?
- 3013A manual fire alarm box serves an exit doorway. Within what distance of the doorway must it be located?
- 3014What is the minimum sound level for an audible public mode evacuation signal in an area with an average ambient sound level of 70 dBA?
- 3015What is the maximum sound pressure level permitted for an audible notification appliance at the minimum hearing distance?
- 3016A sleeping room has an average ambient of 35 dBA and a maximum 60 second level of 45 dBA. What is the minimum required audible signal level at the pillow?
- 3017What signal characteristic does NFPA 72 require for audible alarms intended to wake sleeping occupants in sleeping areas?
- 3018Which signal pattern is required for the standard fire evacuation tone?
- 3019A notification appliance rated at 85 dBA at 10 ft is heard at 20 ft in a free field. Approximately what level reaches the listener at 20 ft?
- 3020Two identical horns each produce 80 dBA at a point. What is the approximate combined level at that point?
- 3021What is the permitted mounting height for wall-mounted visible notification appliances?
- 3022When must visible notification appliances in a room be synchronized?
- 3023Using the room spacing table for a single wall-mounted strobe, what minimum effective intensity is required for a 20 ft by 20 ft room?
- 3024A sleeping room strobe is mounted 18 in below the ceiling. What minimum effective intensity is required?
- 3025In a corridor not more than 20 ft wide, what is the maximum distance from the end of the corridor to the nearest visible appliance?
- 3026What is the minimum secondary power capacity for a protected premises fire alarm system without voice evacuation?
- 3027A fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
- 3028Within what time after an initiating device activates must the fire alarm control unit activate the alarm notification appliances?
- 3029What is the maximum time permitted for alarm verification on a smoke detector circuit?
- 3030Under positive alarm sequence, how long does trained staff have to acknowledge the alarm at the control unit?
- 3031A waterflow alarm initiating device must produce an alarm signal within what time after flow equal to one sprinkler starts?
- 3032A valve supervisory switch must signal an off normal condition within what movement of the valve?
- 3033For elevator shunt trip, where must heat detectors be located relative to sprinklers in the elevator machine room or hoistway?