Question 3008 of 153 · Oklahoma Fire Alarm Technician Exam
A heat detector should have a temperature rating at least how far above the maximum expected ambient ceiling temperature?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3008
- B: 20 degrees F
Explanation
NFPA 72 requires the operating temperature of a heat detector to be at least 20 degrees F above the maximum expected ceiling temperature to avoid nuisance alarms.
More questions: System Layout and NFPA 72 Requirements
- 3009A heat detector frame is colored white. Which temperature classification does this color code indicate?
- 3010NFPA 72 guidance on locating a smoke detector near an air supply diffuser calls for what minimum separation?
- 3011What is the primary purpose of a duct smoke detector in an HVAC system?
- 3012What is the required mounting height for the operable part of a manual fire alarm box?
- 3013A manual fire alarm box serves an exit doorway. Within what distance of the doorway must it be located?
- 3014What is the minimum sound level for an audible public mode evacuation signal in an area with an average ambient sound level of 70 dBA?