Question 3007 of 153 · Oklahoma Fire Alarm Technician Exam
Under a peaked ceiling, where must a row of spot-type smoke detectors be placed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3007
- D: Within 36 in horizontally of the peak
Explanation
For peaked ceilings, a row of detectors goes within 36 in horizontally of the peak, measured from the peak. Additional detectors are then laid out based on the horizontal projection of the ceiling.