Question 3016 of 153 · Oklahoma Fire Alarm Technician Exam
A sleeping room has an average ambient of 35 dBA and a maximum 60 second level of 45 dBA. What is the minimum required audible signal level at the pillow?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3016
- A: 75 dBA
Explanation
In sleeping areas the signal must be the greatest of 15 dB above average ambient (50 dBA), 5 dB above the 60 second maximum (50 dBA), or 75 dBA. The 75 dBA minimum governs.
More questions: System Layout and NFPA 72 Requirements
- 3017What signal characteristic does NFPA 72 require for audible alarms intended to wake sleeping occupants in sleeping areas?
- 3018Which signal pattern is required for the standard fire evacuation tone?
- 3019A notification appliance rated at 85 dBA at 10 ft is heard at 20 ft in a free field. Approximately what level reaches the listener at 20 ft?
- 3020Two identical horns each produce 80 dBA at a point. What is the approximate combined level at that point?
- 3021What is the permitted mounting height for wall-mounted visible notification appliances?
- 3022When must visible notification appliances in a room be synchronized?