Question 3021 of 153 · Oklahoma Fire Alarm Technician Exam
What is the permitted mounting height for wall-mounted visible notification appliances?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3021
- A: Entire lens between 80 in and 96 in above the floor
Explanation
Wall-mounted visible appliances are mounted so the entire lens is not less than 80 in and not more than 96 in above the finished floor, unless listed otherwise or limited by ceiling height.
More questions: System Layout and NFPA 72 Requirements
- 3022When must visible notification appliances in a room be synchronized?
- 3023Using the room spacing table for a single wall-mounted strobe, what minimum effective intensity is required for a 20 ft by 20 ft room?
- 3024A sleeping room strobe is mounted 18 in below the ceiling. What minimum effective intensity is required?
- 3025In a corridor not more than 20 ft wide, what is the maximum distance from the end of the corridor to the nearest visible appliance?
- 3026What is the minimum secondary power capacity for a protected premises fire alarm system without voice evacuation?
- 3027A fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?