What signal characteristic does NFPA 72 require for audible alarms intended to wake sleeping occupants in sleeping areas?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3017
- B: A low frequency square wave tone of about 520 Hz
Explanation
Research showed a 520 Hz low frequency square wave wakes people, including those with hearing loss, far better than the traditional high pitched tone. NFPA 72 requires it for audible alarms in sleeping areas.