Question 4014 of 153 · Oklahoma Fire Alarm Technician Exam
Fire alarm cable is installed in a ceiling space used for environmental air (a plenum). Which cable type is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4014
- A: FPLP
Explanation
Spaces used for environmental air require plenum rated cable, FPLP for power limited fire alarm circuits. FPLR is riser rated and FPL is general purpose.
More questions: Installation, Wiring and Pathways
- 4015Which communications cable type may be substituted for FPLR riser cable?
- 4016What is the minimum conductor size permitted in a multiconductor power limited fire alarm cable?
- 4017What is the main purpose of the equipment grounding conductor connected to a fire alarm control unit?
- 4018Which NEC section requires electrical equipment to be installed in a neat and workmanlike manner?
- 4019According to Article 90, what is the purpose of the NEC?
- 4020Fire alarm cable passes through a 1 hour fire rated wall. What must be done with the opening?