Which pathway class designation covers Ethernet type networks with a redundant pathway monitoring arrangement for fire alarm communication?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4004
- C: Class N
Explanation
Class N was added for modern network infrastructure such as Ethernet. Class C covers pathways supervised through end to end communication, and Class E covers pathways that are not monitored for integrity.