Question 4005 of 153 · Oklahoma Fire Alarm Technician Exam
A survivability Level 2 pathway requires which type of protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4005
- D: A 2 hour fire rated cable, enclosure or equivalent
Explanation
Level 2 survivability uses 2 hour rated circuit integrity cable, 2 hour rated enclosures or performance alternatives. Level 3 adds full sprinkler protection, and Level 1 relies on sprinklers plus metal raceway.
More questions: Installation, Wiring and Pathways
- 4006Which NFPA 70 article governs fire alarm system wiring?
- 4007Power limited fire alarm cable run vertically in a shaft between floors must at least be which type?
- 4008How must the branch circuit disconnecting means for a fire alarm control unit be marked?
- 4009Two wire smoke detectors powered from an initiating device circuit must meet which requirement?
- 4010On a conventional Class B initiating device circuit, a T-tap is added to reach an extra detector. What problem does this create?
- 4011How must power limited fire alarm cable above a suspended ceiling be supported?