Under NFPA 101, a required fire alarm system will be out of service for more than 4 hours in a 24 hour period. What is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5010
- A: Notify the AHJ and evacuate the building or provide an approved fire watch
Explanation
NFPA 101 requires that the AHJ be notified and that the building be evacuated or an approved fire watch be provided for the unprotected areas. NFPA 72 itself sets the impairment procedures; the 4 hour threshold comes from the Life Safety Code.
More questions: Inspection, Testing and Service
- 5011What document is prepared at acceptance to record the installed system details, and is kept for the life of the system?
- 5012What is the frequency for the visual inspection of fire alarm control units in a monitored system?
- 5013How often must a sealed lead acid fire alarm battery receive its load voltage and charger tests?
- 5014During an annual test, a duct smoke detector does not alarm with test smoke. What should the technician check first?
- 5015What is the required frequency for testing a vane type waterflow switch with flow through the inspector's test connection?