Question 5009 of 153 · Oklahoma Fire Alarm Technician Exam
How long must inspection and test records be kept?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5009
- B: Until the next test and for 1 year after that
Explanation
Records of inspections, tests and maintenance are kept until the next test and for 1 year thereafter. The record of completion and acceptance test records are kept for the life of the system.
More questions: Inspection, Testing and Service
- 5010Under NFPA 101, a required fire alarm system will be out of service for more than 4 hours in a 24 hour period. What is required?
- 5011What document is prepared at acceptance to record the installed system details, and is kept for the life of the system?
- 5012What is the frequency for the visual inspection of fire alarm control units in a monitored system?
- 5013How often must a sealed lead acid fire alarm battery receive its load voltage and charger tests?
- 5014During an annual test, a duct smoke detector does not alarm with test smoke. What should the technician check first?
- 5015What is the required frequency for testing a vane type waterflow switch with flow through the inspector's test connection?