A smoke detector shows a dirty or maintenance alert. What is the correct service approach?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5022
- B: Clean or replace it per the manufacturer, then confirm sensitivity is in range
Explanation
Detectors are cleaned using the manufacturer's method or replaced, and sensitivity is confirmed afterwards. Masking the problem at the panel is not acceptable.
More questions: Inspection, Testing and Service
- 5023A Class B initiating circuit with a 4.7 kilohm end of line resistor is disconnected from the panel and measured. The meter shows OL (infinite). What does this indicate?
- 5001What is the required frequency for functional testing of system smoke detectors?
- 5002When must the first sensitivity test of a system smoke detector be performed?
- 5003Which method is NOT acceptable to measure the sensitivity of a smoke detector?
- 5004Nonrestorable fixed temperature spot-type heat detectors have been in service for 15 years. What does NFPA 72 require?
- 5005How should a restorable spot-type heat detector be functionally tested?