Question 5023 of 153 · Oklahoma Fire Alarm Technician Exam
A Class B initiating circuit with a 4.7 kilohm end of line resistor is disconnected from the panel and measured. The meter shows OL (infinite). What does this indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5023
- A: An open in the circuit wiring or a missing resistor
Explanation
A good circuit reads close to the end of line value plus wire resistance. An infinite reading means the path is broken. Near zero ohms would mean a short.