During the annual test of a monitored system, what must be verified with the supervising station?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5021
- D: That it receives the correct alarm, supervisory and trouble signals
Explanation
Testing confirms that the supervising station receives each signal type with the correct identification, not just that a communication path exists.
More questions: Inspection, Testing and Service