A spot-type smoke detector has to be mounted on a sidewall instead of the ceiling. Where must the top of the detector be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1001
- B: Between the ceiling and 12 in. below the ceiling
Explanation
NFPA 72 allows a sidewall spot-type smoke detector anywhere from the ceiling line down to 12 in., measured to the top of the detector. The old 4 in. dead air space rule was dropped for smoke detectors; it still applies to spot-type heat detectors.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1002A spot-type heat detector is being mounted on a smooth ceiling. What is the minimum distance from the sidewall?
- 1003A heat detector must be mounted on a sidewall. Which mounting position meets NFPA 72?
- 1004On a smooth, flat ceiling with no performance-based design, what nominal spacing is used for spot-type smoke detectors?
- 1005Smoke detectors on a smooth ceiling are laid out at a 30 ft nominal spacing. Every point on the ceiling must be within what distance of a detector?
- 1006A heat detector has a listed spacing of 50 ft and is installed on a smooth 9 ft ceiling. What is the maximum distance from any wall to the nearest detector, measured at right angles?
- 1007A heat detector listed for 50 ft spacing is installed on a smooth 15 ft high ceiling. Using the NFPA 72 high ceiling reduction factor of 0.77 for 14 to 16 ft, what is the adjusted spacing?