On a smooth, flat ceiling with no performance-based design, what nominal spacing is used for spot-type smoke detectors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1004
- A: 30 ft
Explanation
Spot-type smoke detectors on smooth ceilings use a nominal spacing of 30 ft. Unlike heat detectors, smoke detectors do not carry a listed spacing, so 30 ft is the prescriptive value. 50 ft is a common listed spacing for heat detectors.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1005Smoke detectors on a smooth ceiling are laid out at a 30 ft nominal spacing. Every point on the ceiling must be within what distance of a detector?
- 1006A heat detector has a listed spacing of 50 ft and is installed on a smooth 9 ft ceiling. What is the maximum distance from any wall to the nearest detector, measured at right angles?
- 1007A heat detector listed for 50 ft spacing is installed on a smooth 15 ft high ceiling. Using the NFPA 72 high ceiling reduction factor of 0.77 for 14 to 16 ft, what is the adjusted spacing?
- 1008The highest expected ceiling temperature in a mechanical room is 120 F. What is the lowest fixed-temperature heat detector rating that may be used?
- 1009A fixed-temperature heat detector is rated 194 F. In which NFPA 72 temperature classification does it fall?
- 1010What color marking identifies a heat detector in the intermediate temperature classification?