Under which ambient condition may a spot-type smoke detector NOT be installed unless it is specifically listed for that condition?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1014
- A: Relative humidity above 93 percent
Explanation
Unless specifically listed, smoke detectors are not to be installed where the temperature is below 32 F or above 100 F, the relative humidity is above 93 percent, or air velocity exceeds 300 ft/min. The other choices are normal room conditions.