At what height must the operable part of a manual fire alarm box be mounted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1018
- A: Not less than 42 in. and not more than 48 in. above the floor
Explanation
The operable part (the handle or lever) of a manual fire alarm box must sit 42 in. to 48 in. above floor level so it is within reach from a wheelchair. The measurement is to the operable part, not to the top of the box.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1019A manual fire alarm box is required at an exit door. Within what distance of the exit doorway opening must it be located?
- 1020On one floor of a building, what is the maximum travel distance from any point to the nearest manual fire alarm box?
- 1021A tenant wants to hide a manual fire alarm box behind a decorative curtain. What does NFPA 72 require?
- 1022A wall-mounted visible notification appliance (strobe) is being hung in a room with a 10 ft ceiling. Where must its lens be?
- 1023A room has a ceiling only 84 in. high, so a wall strobe cannot meet the normal 80 to 96 in. range. Where may it be mounted?
- 1024A wall-mounted horn (audible only) is installed in a room with a 12 ft ceiling. Where must the top of the horn be?