Question 1019 of 299 · NICET Fire Alarm Systems Level I
A manual fire alarm box is required at an exit door. Within what distance of the exit doorway opening must it be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1019
- D: 5 ft
Explanation
Where manual boxes are required at exits, each box is located within 5 ft of the exit doorway opening, so people pull it on their way out. The 200 ft value is the travel distance limit between boxes, not the distance from the door.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1020On one floor of a building, what is the maximum travel distance from any point to the nearest manual fire alarm box?
- 1021A tenant wants to hide a manual fire alarm box behind a decorative curtain. What does NFPA 72 require?
- 1022A wall-mounted visible notification appliance (strobe) is being hung in a room with a 10 ft ceiling. Where must its lens be?
- 1023A room has a ceiling only 84 in. high, so a wall strobe cannot meet the normal 80 to 96 in. range. Where may it be mounted?
- 1024A wall-mounted horn (audible only) is installed in a room with a 12 ft ceiling. Where must the top of the horn be?
- 1025You are mounting a combination horn/strobe on a wall. Which mounting rule controls its height?