A tenant wants to hide a manual fire alarm box behind a decorative curtain. What does NFPA 72 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1021
- C: The box must remain conspicuous, unobstructed and accessible
Explanation
Manual fire alarm boxes must be conspicuous, unobstructed and accessible. A curtain hides the box and slows down anyone trying to raise the alarm, whatever the curtain material.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1022A wall-mounted visible notification appliance (strobe) is being hung in a room with a 10 ft ceiling. Where must its lens be?
- 1023A room has a ceiling only 84 in. high, so a wall strobe cannot meet the normal 80 to 96 in. range. Where may it be mounted?
- 1024A wall-mounted horn (audible only) is installed in a room with a 12 ft ceiling. Where must the top of the horn be?
- 1025You are mounting a combination horn/strobe on a wall. Which mounting rule controls its height?
- 1026The drawings show ceiling-mounted strobes, but the installer looks up the candela rating in the wall-mounted spacing table. What is wrong?
- 1027A 40 ft x 40 ft room will be covered by one wall-mounted strobe. Using the NFPA 72 room spacing table, what is the minimum effective intensity?