What does a Class A pathway provide that a Class B pathway does not?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1037
- A: A redundant return path so a single open does not stop signals
Explanation
A Class A pathway leaves the panel and returns to it, so after a single open the devices can still be reached from both ends and the panel reports a trouble. A Class B pathway has no return path, so devices beyond an open are lost.