A single ground fault occurs on a supervised initiating device circuit. What should the panel do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1041
- D: Indicate a trouble signal without causing an alarm
Explanation
Installation conductors are monitored for integrity, so a single ground fault must be automatically indicated as trouble. It must not cause a false alarm.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1042Within how many seconds must a single open or single ground fault on monitored installation conductors be indicated?
- 1043On a conventional two-wire smoke detector zone, what is the purpose of the detector base wiring when the head is removed?
- 1044Four-wire smoke detectors get their operating power from a separate power circuit. What must be installed to supervise that power?
- 1045A two-wire smoke detector from a different manufacturer is offered as a replacement on an existing conventional zone. What must be confirmed?
- 1046When installing a fire alarm device, which instructions must be followed in addition to the code?
- 1047Two addressable smoke detectors on the same signaling line circuit were accidentally set to the same address. What is the likely result?