Question 1039 of 299 · NICET Fire Alarm Systems Level I
When installing a Class A circuit, how should the outgoing and return conductors be run?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1039
- D: Routed separately, with only the limited exceptions in NFPA 72
Explanation
Class A redundancy only helps if one event cannot damage both paths. NFPA 72 requires the outgoing and return conductors to be routed separately, with a short exception (up to 10 ft) where they enter or leave a device or control unit enclosure.