A two-wire smoke detector from a different manufacturer is offered as a replacement on an existing conventional zone. What must be confirmed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1045
- D: That it is listed as compatible with that control unit
Explanation
Devices that draw their power from an initiating device circuit or signaling line circuit must be listed for use with that control unit. Two-wire detectors depend on the panel's voltage and current limits, so compatibility is not automatic.