Question 1044 of 299 · NICET Fire Alarm Systems Level I

Four-wire smoke detectors get their operating power from a separate power circuit. What must be installed to supervise that power?

Exactly one answer is correct.

Show solution

Correct answer to question 1044

  • A: An end-of-line power supervision relay at the last detector

Explanation

If the 24 V power run to four-wire detectors is lost, the detectors cannot alarm. A power supervision relay at the end of the power run holds a contact in the initiating circuit closed, so loss of power causes a trouble.

Next to question ›