Four-wire smoke detectors get their operating power from a separate power circuit. What must be installed to supervise that power?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1044
- A: An end-of-line power supervision relay at the last detector
Explanation
If the 24 V power run to four-wire detectors is lost, the detectors cannot alarm. A power supervision relay at the end of the power run holds a contact in the initiating circuit closed, so loss of power causes a trouble.