Question 1077 of 299 · NICET Fire Alarm Systems Level I
Where must splices in fire alarm wiring be made?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1077
- C: In a box or listed enclosure that remains accessible
Explanation
Splices and terminations must be in boxes, fittings or listed enclosures, and boxes must remain accessible. Hidden splices are a frequent source of opens and ground faults that are hard to find.
More questions: Installation (Peripherals, Cabling, Job Site Safety)