A shielded cable is used for an addressable loop. Where is the drain wire usually connected?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1078
- A: At one end only, normally at the panel, per the manufacturer
Explanation
Most manufacturers ground the shield at the control panel only and keep it continuous but insulated at devices. Grounding it at several points can create ground loops and ground faults.