Question 1092 of 299 · NICET Fire Alarm Systems Level I
Which conductor has the largest cross section?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1092
- D: 12 AWG
Explanation
In the AWG system a larger gauge number means a smaller wire. 12 AWG is the largest of these choices and has the lowest resistance per foot.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1093A NAC power supply circuit is rated 2.5 A. Each strobe draws 0.12 A. How many strobes can be connected without exceeding the rating?
- 1094Two 12 V, 7 Ah batteries are connected in series for a 24 V panel. What is the result?
- 1095A 24 V NAC can tolerate a maximum voltage drop of 3 V. Total load is 2 A on 14 AWG wire with 3.07 ohm per 1,000 ft. What is the maximum one-way circuit length?
- 1096A 24 V circuit carries 0.5 A. What resistance does the load have?
- 1097What type of power does a typical fire alarm control unit use for its primary supply and for its notification circuits?
- 1098You set up an extension ladder to reach a mezzanine landing. How far must the side rails extend above the upper landing surface?