A NAC power supply circuit is rated 2.5 A. Each strobe draws 0.12 A. How many strobes can be connected without exceeding the rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1093
- D: 20
Explanation
2.5 A / 0.12 A = 20.8, so 20 strobes (2.40 A) fit and 21 would draw 2.52 A, over the rating. Always round down when the limit cannot be exceeded.