A sprinkler system serves an elevator machine room and the elevator power is shunt tripped on waterflow. Where must the heat detectors for elevator shutdown be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1144
- C: Within 2 ft of each sprinkler in the space
Explanation
Where heat detectors are used to shut down elevator power before sprinkler discharge, each one is placed within 2 ft of each sprinkler head. Their rating is lower than the sprinkler rating so power shuts off first.