Question 1144 of 299 · NICET Fire Alarm Systems Level I

A sprinkler system serves an elevator machine room and the elevator power is shunt tripped on waterflow. Where must the heat detectors for elevator shutdown be located?

Exactly one answer is correct.

Show solution

Correct answer to question 1144

  • C: Within 2 ft of each sprinkler in the space

Explanation

Where heat detectors are used to shut down elevator power before sprinkler discharge, each one is placed within 2 ft of each sprinkler head. Their rating is lower than the sprinkler rating so power shuts off first.

Next to question ›