Where must a relay or control module that performs an emergency control function, such as fan shutdown, be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1143
- A: Within 3 ft of the component, or with monitored wiring
Explanation
NFPA 72 requires the relay or other interface device for an emergency control function to be within 3 ft of the controlled component, unless the wiring between them is monitored for integrity, so unmonitored wiring stays short.