Nonrestorable spot-type fixed-temperature heat detectors have been in service for 15 years. What is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2009
- A: Replace them, or lab test 2 detectors per 100
Explanation
After 15 years, nonrestorable spot-type fixed-temperature heat detectors are replaced or two out of every 100 are laboratory tested. If a sample fails, more detectors are tested or all are replaced.