Nonrestorable spot-type fixed-temperature heat detectors have been in service for 15 years. What is required?

Exactly one answer is correct.

Show solution

Correct answer to question 2009

  • A: Replace them, or lab test 2 detectors per 100

Explanation

After 15 years, nonrestorable spot-type fixed-temperature heat detectors are replaced or two out of every 100 are laboratory tested. If a sample fails, more detectors are tested or all are replaced.