A waterflow switch is tested by opening the inspector's test valve. What flow is the test meant to simulate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2015
- B: The flow from a single sprinkler of the smallest orifice in the system
Explanation
The inspector's test connection simulates one sprinkler of the smallest orifice size. The fire alarm system should receive the waterflow signal within 90 seconds of flow.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2016During a tamper switch test you close the valve. When should the supervisory signal clear?
- 2017Before starting a test that will activate initiating devices, who must be notified?
- 2018You have finished testing a building and restored the system. What notification is required at the end?
- 2019Who is responsible for making sure a fire alarm system is inspected, tested and maintained?
- 2020How long must inspection and test records be kept?
- 2022After a new device is installed on an existing system, what testing is required?