A building has 300 nonrestorable spot-type heat detectors that are 15 years old. The owner chooses lab testing instead of replacement. How many detectors must be sent for testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2010
- B: 6
Explanation
The rule is two detectors per 100: 300 / 100 x 2 = 6. If any fails, additional detectors are tested per the code.