Question 2020 of 299 · NICET Fire Alarm Systems Level I
How long must inspection and test records be kept?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2020
- C: Until the next test of the same type and 1 year after it
Explanation
Records of inspection and testing are retained until the next test of the same kind and for 1 year after that, so there is always a full test cycle on file for the AHJ.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2022After a new device is installed on an existing system, what testing is required?
- 2023The site-specific software of a control unit was changed. Besides the functions known to be affected, how many other initiating devices must be tested?
- 2024What is the purpose of the 100 percent acceptance test on a new fire alarm system?
- 2025At acceptance testing, how are installation conductors checked for unwanted voltages?
- 2026To measure loop resistance of an initiating device circuit during acceptance testing, what is done at the far end of the circuit?
- 2027A technician checks fire alarm conductors for isolation from ground. What is being looked for?