Why must resistance measurements be made with the circuit de-energized?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2031
- D: Voltage in the circuit gives false readings and can damage the meter
Explanation
An ohmmeter uses its own small battery voltage. Any outside voltage on the circuit corrupts the reading and may damage the meter, so the circuit is disconnected from the panel first.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2032You disconnect a Class B initiating device circuit at the panel and measure across the pair. The meter shows about 4,700 ohm, matching the EOL value. What does this tell you?
- 2033Measured across a disconnected Class B circuit pair, the meter shows OL (over limit). What is the most likely problem?
- 2034Across a disconnected initiating circuit pair, the meter reads close to 0 ohm. What is the most likely problem?
- 2035A panel shows a ground fault. Which technique is commonly used to locate it on a long circuit?
- 2036What sound level meter weighting is used to measure fire alarm audibility?
- 2037At what height above the floor are audibility measurements normally taken?