Question 2032 of 299 · NICET Fire Alarm Systems Level I

You disconnect a Class B initiating device circuit at the panel and measure across the pair. The meter shows about 4,700 ohm, matching the EOL value. What does this tell you?

Exactly one answer is correct.

Show solution

Correct answer to question 2032

  • D: The circuit is continuous to the EOL with no short

Explanation

Reading the EOL value from the panel end means current can flow out to the resistor and back, so the circuit is neither open nor shorted. A ground fault check is a separate measurement to ground.

Next to question ›