You disconnect a Class B initiating device circuit at the panel and measure across the pair. The meter shows about 4,700 ohm, matching the EOL value. What does this tell you?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2032
- D: The circuit is continuous to the EOL with no short
Explanation
Reading the EOL value from the panel end means current can flow out to the resistor and back, so the circuit is neither open nor shorted. A ground fault check is a separate measurement to ground.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2033Measured across a disconnected Class B circuit pair, the meter shows OL (over limit). What is the most likely problem?
- 2034Across a disconnected initiating circuit pair, the meter reads close to 0 ohm. What is the most likely problem?
- 2035A panel shows a ground fault. Which technique is commonly used to locate it on a long circuit?
- 2036What sound level meter weighting is used to measure fire alarm audibility?
- 2037At what height above the floor are audibility measurements normally taken?
- 2038The average ambient sound level in a store is 62 dBA. What minimum fire alarm sound level is needed for public mode, if no louder short-term noise is present?